Report Tag Problem
So...I have two report tags reporting 15 analog inputs on a standard style report, outputing to a CSV file in a folder on a server. Custom preset at 1 second duration, and 1 minute end time. The report tags are triggered daily at 1:55pm, and 4:55am. The reports successfully generate but only with time/date information and analog input tag names...no values. Any ideas on where I might be going wrong?
I would change your tags to be analog status and configure logging with a deadband of 0 to start. When you've verified that the tags are historizing data correctly (have data) at the exact timestamp up the reports are running, you should have data on you reports.
edited Mar 7 at 6:24 pm
As Michael noted, by default an Analog Input tag has no logger attached, you have to configure a separate tag to do that.
An Analog Status has a built-in logger.
As Michael noted, by default an Analog Input tag has no logger attached, you have to configure a separate tag to do that. An Analog Status has a built-in logger.
40
