Is there a way to send unacknowledged or new alarm status back to a PLC bit?

Is there a way to send unacknowledged or new alarm status back to a PLC bit?

You can use the Alarm Status Tag to look for an active alarm, link that to a Digital Control Tag via the Data Source field of the Digital Control Tag. In the Address field of the Digital Control Tag write to the PLC and append the address with a data suffix to write to a specific bit. Please see the links below for more help on this:

Alarm Status Tags:
https://www.trihedral.com/help/Content/D_Tags/Alarm-Status-Tag.htm

Digital Control Tags:
https://www.trihedral.com/help/Content/D_Tags/Dev_DigitalControl.htm

Data Suffix:
https://www.trihedral.com/help/Content/D_Tags/Dev_DataSuffixesForTagIO.htm

I hope this helps. Please follow up if you have other questions

You can use the Alarm Status Tag to look for an active alarm, link that to a Digital Control Tag via the Data Source field of the Digital Control Tag. In the Address field of the Digital Control Tag write to the PLC and append the address with a data suffix to write to a specific bit. Please see the links below for more help on this: Alarm Status Tags: https://www.trihedral.com/help/Content/D_Tags/Alarm-Status-Tag.htm Digital Control Tags: https://www.trihedral.com/help/Content/D_Tags/Dev_DigitalControl.htm Data Suffix: https://www.trihedral.com/help/Content/D_Tags/Dev_DataSuffixesForTagIO.htm I hope this helps. Please follow up if you have other questions

Trihedral Engineering Ltd.