This depends on how you have your tag set. Your Digital Control tag will have a Pulse Duration input box in the I/O tab. If that is set to zero, the tag will write the set value to the address you choose. If there is a pulse defined, the tag will write a 1 (or your defined value) and then a 0. It is common to use two buttons, both having a pulse of 0. One to write a 1 and the other to write a 0. You can define the value to write in the button properties
Does that make sense?
This depends on how you have your tag set. Your Digital Control tag will have a Pulse Duration input box in the I/O tab. If that is set to zero, the tag will write the set value to the address you choose. If there is a pulse defined, the tag will write a 1 (or your defined value) and then a 0. It is common to use two buttons, both having a pulse of 0. One to write a 1 and the other to write a 0. You can define the value to write in the button properties