Hello.
I think there is some bug related to the Selector Switches. I have spent countless hours on this, and by accident found a way to make it work. Meaning this must be some bug.
If I make more than a couple Selector Switches, the next one appear with no data. Like 40310 below. I have the exact same settings, because I copy the working Switch. I only change the adress.
Scanning for the 40310 Modbus adress with CAS:
Reading the bit with digital input:
Selector Switch is still not working:
If I however enter ANY digital tag in Feedback.
Then the Switch will show Auto, as the digital input was 1.
But if I remove the Feedback, the Switch still works.
And now I can toggle the switch as expected.
Hello.
I think there is some bug related to the Selector Switches. I have spent countless hours on this, and by accident found a way to make it work. **Meaning this must be some bug.**
If I make more than a couple Selector Switches, the next one appear with no data. Like 40310 below. I have the exact same settings, because I copy the working Switch. I only change the adress.
![59a56673dd99c.png](serve/attachment&path=59a56673dd99c.png)
Scanning for the 40310 Modbus adress with CAS:
![59a566fe463e2.png](serve/attachment&path=59a566fe463e2.png)
Reading the bit with digital input:
![59a56750848f8.png](serve/attachment&path=59a56750848f8.png)
Selector Switch is still not working:
![59a5679bbae9c.png](serve/attachment&path=59a5679bbae9c.png)
If I however enter ANY digital tag in Feedback.
![59a567efc2d10.png](serve/attachment&path=59a567efc2d10.png)
Then the Switch will show Auto, as the digital input was 1.
![59a5682bcf489.png](serve/attachment&path=59a5682bcf489.png)
But if I remove the Feedback, the Switch still works.
![59a568572e803.png](serve/attachment&path=59a568572e803.png)
And now I can toggle the switch as expected.
![59a5695776af8.gif](serve/attachment&path=59a5695776af8.gif)