Modbus 32 bit value

Is there a way to read a 32 bit modbus value directly into a 32 bit value in VTSCADA? This way we will not need to read a 32 bit value as 2 single 16 bit values and then combine it.

Is there a way to read a 32 bit modbus value directly into a 32 bit value in VTSCADA? This way we will not need to read a 32 bit value as 2 single 16 bit values and then combine it.

Check out "Data Suffixes for Tag I/O Addressing" in the help files. But, yes...

40001/Float, 40001/SDWORD, 40001/UDWORD will bring in 32 bit floats, soigned and unsigned integers.

Check out "Data Suffixes for Tag I/O Addressing" in the help files. But, yes... 40001/Float, 40001/SDWORD, 40001/UDWORD will bring in 32 bit floats, soigned and unsigned integers.