Alarm Acknowledgement

In VTscada, is there a way to link a tag to an alarm acknowledgement button in the alarm window that can turn on or off a tag in the PLC?

Thanks.

In VTscada, is there a way to link a tag to an alarm acknowledgement button in the alarm window that can turn on or off a tag in the PLC? Thanks.

We use two additional tags for every alarm to manage this.

An Alarm List tag to monitor a filtered alarm list transitioning from 1 to 0 alarms, and an IO tag which writes to a handshake bit that monitors the Alarm List tag, unlatching the alarm in the PLC.

We use two additional tags for every alarm to manage this. An Alarm List tag to monitor a filtered alarm list transitioning from 1 to 0 alarms, and an IO tag which writes to a handshake bit that monitors the Alarm List tag, unlatching the alarm in the PLC.

Got this to work using your technique, thanks, very helpful!

Got this to work using your technique, thanks, very helpful!