I want to establish a connection with a Siemens Logo! 8 PLC and in VTScada I use the Siemens S7-200 driver, Rack 0 Slot 2, CP Type None, ISO Over TCP.

What are the TSAP values I have to use in the connection setting of the LOGO 8 module (Its a somewhat older model at FS2 level)
and what is the memory mapping I must use to read Flag M1

I want to establish a connection with a Siemens Logo! 8 PLC and in VTScada I use the Siemens S7-200 driver, Rack 0 Slot 2, CP Type None, ISO Over TCP. What are the TSAP values I have to use in the connection setting of the LOGO 8 module (Its a somewhat older model at FS2 level) and what is the memory mapping I must use to read Flag M1

Thanks for your help and I will also try to connect via Modbus TCP but I managed to make a connection to the Logo PLC via the S7 driver!

My settings for Logo!8:
Firmware version 0BA8 Standard V1.08.02

Ethernet Connection
Local Properties (Server) TSAP 20.00
Remote Properties (Client) TSAP 03.02

Communication with VTScada in my test setup via Flags M1, M2 and VM Word addres 2.

For VTScada the connection is made via TCP/IP Port Number 102 and Driver Siemens S7 PLC Options: S7-200, ISO over TCP, OP Mode, Rack 0 Slot 2, CP Type None, Store Last Output Values.
and I can write to input Flag M1 via address M0.0, read from output Flag M1 via address M0.1 and Read/Write to VM word address 2 via address VW1.

Thanks for your help and I will also try to connect via Modbus TCP but I managed to make a connection to the Logo PLC via the S7 driver! My settings for Logo!8: Firmware version 0BA8 Standard V1.08.02 Ethernet Connection Local Properties (Server) TSAP 20.00 Remote Properties (Client) TSAP 03.02 Communication with VTScada in my test setup via Flags M1, M2 and VM Word addres 2. For VTScada the connection is made via TCP/IP Port Number 102 and Driver Siemens S7 PLC Options: S7-200, ISO over TCP, OP Mode, Rack 0 Slot 2, CP Type None, Store Last Output Values. and I can write to input Flag M1 via address M0.0, read from output Flag M1 via address M0.1 and Read/Write to VM word address 2 via address VW1.