Jerry
posted Jun 8 '22 at 8:00 am
On the same computer, VTScada as OPC DA server, Kepserver as OPC DA client, OPC DA client is added to kepServer. When adding Select Import Items,The message Failed to connect is displayed as shown in the following figure. Thank you
Hello
I am trialling VT Scada and trying to connect to a B&R PLC running an OPC UA server.
I am able to set everything up but get no data back on the tags. Is this a certification thing?
Has anyone else successfully set up VT Scada with a B&R PLC?
Thanks
Simon
I downloaded VTScada to try out with a Delta PLC, Delta is what we primarily use. According to a PDF on Delta's website there should be the ability to add a Delta Driver in the Tag Browser. The Delta driver isn't listed as one I can add. Here are the instructions I found on Delta's website. Anyone figured this out?
https://filecenter.deltaww.com/Products/download/06/060711/Manual/DELTA_IA_OMS_
Started creating tags that will be connecting to a Siemens PLC and I am getting an error about Tag Address I'm using. Can someone tell me what;s wrong with this PLC tag's address format?
Could there be an issue in the Siemen's tag driver settings?
Does VTScada's built in e-mail client meet the security requirements Google describe
here ---> https://support.google.com/accounts/answer/6010255#more-secure-apps-how
and here ---> https://support.google.com/accounts/answer/3466521
Many of our customers are using gmail to send alarm notifications. We've upgraded some of them to VTScada and are not sure what will happen when google
Hi, i would like to open a pdf with the program spawn widget. I put the path of he file and its still dosnt work. Do i need to put Program.exe before the pdf name?
how can I upload a local file with VTScada script "SYSTEM.HTTPClient.HTTPSend" to a remote webapi server ?
Whould you like give me a sample? thank.
abec34
posted May 26 '22 at 11:46 pm
I am receiving a value of 273 from the BACnet driver but within Wireshark capture I am getting no errors and can see the correct Value being returned.
Any idea why VTScada is giving out an error code of 273? The tag I created has no value which I am assuming since the driver is getting a value of 273 and not 0?
Here is what VTScada is showing:
but here is the proper value comin
When you right-click on a widget, a navigator pop-up open with option like ''Help'' , ''Disable Low Alarm'' ect. I want to custom the label.
I dont find exemple of the navigator script i can use.
acooper
posted May 28 '22 at 4:15 am
Hi all,
This whole OT/ICS world is pretty new to me but I am trying to pick it up and work my way through it, but just looking for a bit of help with something.
I am trying to set up a virtual lab to demo how easy it can be for a hacker to change values and mess with OT equipment if the network is not correctly secure. Originally this was just with getting remote access to a private comp
Tames
posted May 25 '22 at 9:38 pm
I have noticed that if I am using a text box that I am unable to type ".00" to the end of a number, really any length of that .0, .000, etc. If I type it in the program automatically removes it.
It is a small thing but it creates uniform numbers when I have to list of a few of them and the rest have single or double decimal places.
If there is a way to turn that function off?
hardyb
posted May 23 '22 at 3:50 pm
Trying to scale/read a level (0-125)ft reading from a pressure sensor with a range (0.625-25)bar. Trying to figure out my unscaled and scaled values. Pressure sensor signal is 4-20mA.
abec34
posted May 10 '22 at 10:19 pm
Hello,
I am having a really difficult time getting the BACnet Driver to make a connection to an MGate 5217 from MOXA which is a BACnet to Modbus gateway. I am very new to VTScada light but I was able to get the Modbus driver on VTScada to work so I know I am close.
With the BACnet driver. I am not sure if the IP address of the UDP port should be the loopback IP address of (127.0.0.1) or i
Armsp0
posted May 14 '22 at 11:54 pm
Using the tag scaling function does not allow for the 4mA offset of my 4-20mA loop field devices. I'm guessing that this needs to be allowed for by performing a calculation. I check the calculation box in the tag properties window, this causes the IO and scaling tabs to disappear and a calculations tab is substituted. There seems to be little guidance for using this feature. Perhaps I am on the w
Tames
posted May 11 '22 at 5:50 pm
Hello,
I have an odd problem currently where I am trying to link a text to the output value of a multi-write tag. In the text properties I am setting it to 'linked tag properties' and then finding the appropriate tag and then selecting "OutputValue1" (I am assuming this would be the result of the value field in the 1st row of the output tags.)
The problem is that after I select this the
Tames
posted May 5 '22 at 8:17 pm
Hello,
I have a RDP site that I have access to and when I am connected and try to open VTS I get the following dialogue pop up.
I cannot find any information about this error in the help files or online.
Any assistance would be greatly appreciated.
Thanks.
Tyler
Tames
posted Apr 25 '22 at 10:33 pm
I have a site that has two RDP connections, currently both are being run as a 'service' type so I can access them via the webpage (anywhere client) and view the interface pages. The only issue is that I need to edit the graphics for these sites.
As far as I can find in the help documents one of these RDP's needs to be running as an application in order to access the graphics Idea Studio.
in the SQLQuery help page, there is a section "The current values of a tag may be retrieved using a table name with the format "TagName_Current". This table will have one row whose columns are Timestamp (the current time) and the current values of each logged value in the tag.".
How do I use the "TagName_Current"? Can you give me an example? Thanks.
Tames
posted Apr 21 '22 at 6:20 pm
Inside the studio there are the default shapes in the shape tab. When using these shapes I noticed that the only shapes with the options for Fill Pattern, Fill Pattern Color, Outline Line Width, and Outline Line Style (see image below) are only available on the Rounded Rectangle (the default 4 corner, and the default 2 corner) is there a way to get these options on the other shapes? It would be n
Tames
posted Apr 20 '22 at 10:28 pm
I have a site Operator that primarily used the VTScada Anywhere web login to view a site. When viewing the site the pages are too large for the window. Right now they have to hit Ctrl- to zoom out to 90% in order to see the while page.
I logged onto the application server and changed the settings in the Display tab
Resizable window --> Enable
Constrain aspect ratio --> En